• R 3rd party lithium battery replacements safe & OK 2 use?

    From Ant@3:633/280.2 to All on Thu Apr 3 07:20:54 2025
    Are those third party lithium battery replacements (e.g., https://a.co/d/bjBzSf4) safe and good to use for APC UPSes?
    --
    "It is because of him that you are in Christ Jesus, who has become for us wisdom from God--that is, our righteousness, holiness and redemption." --1 Corinthians 1:30. OK, let's stop being fools on hump day. :P
    Note: A fixed width font (Courier, Monospace, etc.) is required to see this signature correctly.
    /\___/\ Ant(Dude) @ http://aqfl.net & http://antfarm.home.dhs.org.
    / /\ /\ \ Please nuke ANT if replying by e-mail.
    | |o o| |
    \ _ /
    ( )

    --- MBSE BBS v1.1.1 (Linux-x86_64)
    * Origin: A noiseless patient Spider (3:633/280.2@fidonet)
  • From Paul@3:633/280.2 to All on Thu Apr 3 12:43:22 2025
    On Wed, 4/2/2025 4:20 PM, Ant wrote:
    Are those third party lithium battery replacements (e.g., https://a.co/d/bjBzSf4) safe and good to use for APC UPSes?


    "The operating current of 12V 10Ah battery is 10A,
    and the maximum instantaneous current is 30A(5 seconds)."

    That means the battery can put out 120W continuously.

    Now, work out the max power output of the APC = 650W

    You're running a 650W UPS using a 120W (continuous) battery.
    That does not sound right, somehow :-) And do you really want
    to leave four or five additional batteries sitting on your
    night table ? I think not.

    The UPS will float charge them constantly at 13.5V .
    Lithium do not float charge (officially, you're not
    supposed to do that). Proper lithium charging requires the
    charger to stop... and not start charging again, until the battery
    is discharged somewhat. The APC does not know you have connected
    LFP -- it is not a mind reader.

    LFP (LiFeP04) chemistry is specifically selected for this product,
    due to its "tolerance of abuse". NMC could not be abused
    like this. You can put current into LFP, even when it
    does not want the current. LFP has lower power density and the ability
    to be abused on its charge cycle. It also has a slightly
    higher charge cycle count than laptop batteries do (if you treat
    them right). These cells are not used in laptops or inside phones
    (not enough runtime, lower power density).

    I don't really know, how to gauge when one of these is failing.
    Sure, it might fail the once-a-day impedance test (which
    lasts for a second or two), but how beat to death would
    this particular battery chemistry be, when it triggers the
    "beep" thing ? APC UPS only beep once on an impedance failure.

    You can tell when an APC SPS (Standby Power Supply) UPS is
    failing, by the metal case temperature. An ice-cold APC SPS
    is working properly. If the APC gets lukewarm to the touch,
    that means your lead acid pack has shorted-out cells inside.
    Time to replace, when the housing gets even a bit warm.
    The SPS type does not dissipate power when in quiet mode,
    which is why it can be cold like that. When it floats the
    battery at 13.5V, hardly any current flows into a "healthy" battery.
    Maybe 5-10mA. How much current flows into the LFP pack ???
    I don't know. And my livingroom seems a poor place for
    pyrotechnical experiments.

    *******

    The price of a kilowatt hour of battery has dropped a lot over time.
    This battery is priced as if the price had never dropped. It's still
    a thousand bucks. You can put eight of these in parallel, but the advert
    says the battery is limited to 50A discharge current (instead of the
    100A by itself). With eight of those in parallel, you get 400A continuous.
    You can put two of the batteries in series, making 24V @ 100A. But at that price, you won't be doing that. And because it has a pushbutton control,
    you won't be buying that (it likely means a BMS test circuit is being
    used as a power control). Batteries have cells, but they have a BMS
    (Battery Management System) circuit board on top which monitors the
    cells and may attempt to "balance" the battery during charging.

    https://batterybrands.com.au/products/pylontech-rv12100-12-8v-100ah-1280wh-4s4p-lifepo4-battery-soc-indicator-m8-terminals-max-2s-or-8p-ip20-rating

    At the price of those batteries, you don't abuse those with a float charge.
    You would use a proper Lithium charger that cuts off the charger when
    the pack is full. It would not fit into your APC, but it would be
    a bit closer to the correct capacity numbers. And it's $1000 so you
    won't be buying that anyway.

    The State of Charge (SoC) indicator on that pack, is four LEDs and a push button.
    You press the switch, and if four LEDs light up, the battery is full. Take
    your finger off the test button and the LEDs stop illumination. Some laptop packs used to have a SoC like that on them. Four LEDs.

    If I could find an authoritative source claiming "this was OK for X years",
    I would tell you that. So far, I haven't seen a BatteryUniversity.com app note on this. That's our source of non-pyrotechnical battery operation info :-)

    I believe some domestic Japanese UPS are using Lithium. I haven't checked lately, to see if anyone in North America has had the cheek to do that
    (fire risk). No, you can't buy the Japanese one as it is the wrong voltage. That helps prevent grey-market sales of such. When they are good and
    ready to make a 115V one, they'll make one.

    Since they are constantly working on new battery designs, I believe one
    day, we will be shed of the 3-year-drop-dead Lead Acid ones and we will
    get a quality design. But it's not ready quite yet. Solid state electrolyte Li is one possible type. Expect abusive pricing on the batteries, as the
    batteries will never match lead acid on price. People insist on selling
    $100 per kWh batteries for $1000 per kWh. "Bad monkey bad".

    Paul

    --- MBSE BBS v1.1.1 (Linux-x86_64)
    * Origin: A noiseless patient Spider (3:633/280.2@fidonet)
  • From Ant@3:633/280.2 to All on Fri Apr 4 06:50:59 2025
    Paul <nospam@needed.invalid> wrote:
    On Wed, 4/2/2025 4:20 PM, Ant wrote:
    Are those third party lithium battery replacements (e.g., https://a.co/d/bjBzSf4) safe and good to use for APC UPSes?

    "The operating current of 12V 10Ah battery is 10A,
    and the maximum instantaneous current is 30A(5 seconds)."

    That means the battery can put out 120W continuously.

    Now, work out the max power output of the APC = 650W

    You're running a 650W UPS using a 120W (continuous) battery.
    That does not sound right, somehow :-) And do you really want
    to leave four or five additional batteries sitting on your
    night table ? I think not.

    The UPS will float charge them constantly at 13.5V .
    Lithium do not float charge (officially, you're not
    supposed to do that). Proper lithium charging requires the
    charger to stop... and not start charging again, until the battery
    is discharged somewhat. The APC does not know you have connected
    LFP -- it is not a mind reader.

    LFP (LiFeP04) chemistry is specifically selected for this product,
    due to its "tolerance of abuse". NMC could not be abused
    like this. You can put current into LFP, even when it
    does not want the current. LFP has lower power density and the ability
    to be abused on its charge cycle. It also has a slightly
    higher charge cycle count than laptop batteries do (if you treat
    them right). These cells are not used in laptops or inside phones
    (not enough runtime, lower power density).

    I don't really know, how to gauge when one of these is failing.
    Sure, it might fail the once-a-day impedance test (which
    lasts for a second or two), but how beat to death would
    this particular battery chemistry be, when it triggers the
    "beep" thing ? APC UPS only beep once on an impedance failure.

    You can tell when an APC SPS (Standby Power Supply) UPS is
    failing, by the metal case temperature. An ice-cold APC SPS
    is working properly. If the APC gets lukewarm to the touch,
    that means your lead acid pack has shorted-out cells inside.
    Time to replace, when the housing gets even a bit warm.
    The SPS type does not dissipate power when in quiet mode,
    which is why it can be cold like that. When it floats the
    battery at 13.5V, hardly any current flows into a "healthy" battery.
    Maybe 5-10mA. How much current flows into the LFP pack ???
    I don't know. And my livingroom seems a poor place for
    pyrotechnical experiments.

    *******

    The price of a kilowatt hour of battery has dropped a lot over time.
    This battery is priced as if the price had never dropped. It's still
    a thousand bucks. You can put eight of these in parallel, but the advert
    says the battery is limited to 50A discharge current (instead of the
    100A by itself). With eight of those in parallel, you get 400A continuous. You can put two of the batteries in series, making 24V @ 100A. But at that price, you won't be doing that. And because it has a pushbutton control,
    you won't be buying that (it likely means a BMS test circuit is being
    used as a power control). Batteries have cells, but they have a BMS
    (Battery Management System) circuit board on top which monitors the
    cells and may attempt to "balance" the battery during charging.

    https://batterybrands.com.au/products/pylontech-rv12100-12-8v-100ah-1280wh-4s4p-lifepo4-battery-soc-indicator-m8-terminals-max-2s-or-8p-ip20-rating

    At the price of those batteries, you don't abuse those with a float charge. You would use a proper Lithium charger that cuts off the charger when
    the pack is full. It would not fit into your APC, but it would be
    a bit closer to the correct capacity numbers. And it's $1000 so you
    won't be buying that anyway.

    The State of Charge (SoC) indicator on that pack, is four LEDs and a push button.
    You press the switch, and if four LEDs light up, the battery is full. Take your finger off the test button and the LEDs stop illumination. Some laptop packs used to have a SoC like that on them. Four LEDs.

    If I could find an authoritative source claiming "this was OK for X years",
    I would tell you that. So far, I haven't seen a BatteryUniversity.com app note
    on this. That's our source of non-pyrotechnical battery operation info :-)

    I believe some domestic Japanese UPS are using Lithium. I haven't checked lately, to see if anyone in North America has had the cheek to do that
    (fire risk). No, you can't buy the Japanese one as it is the wrong voltage. That helps prevent grey-market sales of such. When they are good and
    ready to make a 115V one, they'll make one.

    Since they are constantly working on new battery designs, I believe one
    day, we will be shed of the 3-year-drop-dead Lead Acid ones and we will
    get a quality design. But it's not ready quite yet. Solid state electrolyte Li
    is one possible type. Expect abusive pricing on the batteries, as the batteries will never match lead acid on price. People insist on selling
    $100 per kWh batteries for $1000 per kWh. "Bad monkey bad".

    Thanks Paul. I was debating to get new APC Replacement Battery Cartridge (APCRBC124) battery replacements for my old 865 watts APC Back-UPSes: XS
    1500 (model: BX1500G) and APC Back-UPS XS 1500 (model BX1500G). One of
    them show a blinking battery icon due to its old age. :(
    --
    "Whatever you have learned or received or heard from me, or seen in me ? put it into practice. And the God of peace will be with you." --Philippians 4:9. Flow movie was beautiful with an odd ending.
    Note: A fixed width font (Courier, Monospace, etc.) is required to see this signature correctly.
    /\___/\ Ant(Dude) @ http://aqfl.net & http://antfarm.home.dhs.org.
    / /\ /\ \ Please nuke ANT if replying by e-mail.
    | |o o| |
    \ _ /
    ( )

    --- MBSE BBS v1.1.1 (Linux-x86_64)
    * Origin: A noiseless patient Spider (3:633/280.2@fidonet)
  • From Paul@3:633/280.2 to All on Fri Apr 4 07:24:03 2025
    On Thu, 4/3/2025 3:50 PM, Ant wrote:


    Thanks Paul. I was debating to get new APC Replacement Battery Cartridge (APCRBC124) battery replacements for my old 865 watts APC Back-UPSes: XS 1500 (model: BX1500G) and APC Back-UPS XS 1500 (model BX1500G). One of
    them show a blinking battery icon due to its old age. :(


    The substitution of LiFePO4 for lead acid is a tempting one,
    but I've seen nothing substantial regarding "what could happen".
    Someone suggested "4S4P could work as an automotive battery replacement"
    some time ago, but I've never seen an authoritative analysis of
    the risk level associated with the idea.

    And if a battery with enough amperes to do the job for that size
    of UPS costs $1000, the idea is a non-starter. Lead acid has
    pretty good current flow capability, for a cheap battery type.
    Power-type LiCo could also work (they have twice the amperes of
    kilowatt-hour LiCo cells), but then the risk of fire goes up.
    LiCo will not accept any abuse. LiFePO4 will accept abuse.

    On a car battery, the terminal voltage drops from 12.6V (charged
    and settled) to 9.5V, when the load is 150 amps. That's to give
    you some idea what the impedance of the battery is. The drop
    across the battery (~3 volts) and 150 amps, means the battery
    develops 450 watts of heat inside it during that 5-10 second discharge.

    The Lithium can have a different impedance characteristic,
    but it could also be more sensitive to heat than the
    lumpy lead acid solution.

    If this idea was a big win, they would have done it already
    and these would be fitted to product at the store. I expect
    it is the cost which is unattractive. Once the battery manufacturing
    capability exceeds the market size, the price will drop
    closer to reality.

    Paul


    --- MBSE BBS v1.1.1 (Linux-x86_64)
    * Origin: A noiseless patient Spider (3:633/280.2@fidonet)
  • From Bill Bradshaw@3:633/280.2 to All on Sat Apr 5 05:59:58 2025
    Ant wrote:
    Are those third party lithium battery replacements (e.g., https://a.co/d/bjBzSf4) safe and good to use for APC UPSes?
    o o| |
    \ _ /
    ( )

    It has been a while but the last time I took the batteries to Batteries Plus and they provided replacements for a cost and took the old ones.
    --
    <Bill>

    Brought to you from Anchorage, Alaska



    --- MBSE BBS v1.1.1 (Linux-x86_64)
    * Origin: ---:- FTN<->UseNet Gate -:--- (3:633/280.2@fidonet)